Using the temperature correction factor for the winding insulation temperature graph illustrated what would be the correction factor and the corrected temperature to 40 degrees C for a motor with a insulation resistance of 4 megohms measured at 30 degrees C?
A) The temperature correction factor is 2 and the corrected resistance is 8 megohms at 40 degrees C.
B) The temperature correction factor is 2 and the corrected resistance is 2 megohms at 40 degrees C.
C) The temperature correction factor is 0.5 and the corrected resistance is 8 megohms at 40 degrees C.
D) The temperature correction factor is 0.5 and the corrected resistance is 2 megohms at 40 degrees C.