Log In


Engine_2014 : Electricity - 2283/2299
Get a hint
« Previous Question
You are checking the supply chilled water temperature thermistor probe on a high-pressure hermetic centrifugal chiller. Using the illustrated chart, what statement is true if the supply water temperature is verified 45 ° F with a digital thermometer.
A) When checked with control power on and the thermistor probe connected into the circuit, the thermistor probe voltage drop should be 11.416 volts.
B) When checked with control power on and the thermistor probe isolated, the thermistor probe voltage drop should be 3.805 volts.
C) When checked with control power on and the thermistor probe connected into the circuit, the thermistor probe voltage drop should be 3.805 volts.
D) When checked with control power off and the thermistor probe isolated, the thermistor probe voltage drop should be 3.805 volts.
loading answer...
Illustration EL-0020

Click to view image

Comments
There are no comments for this question.
0 0 0%

Study Mode
Answers Only
Options
Clear Score