If the needle and seat assembly is excessively eroded, the valve cage assembly can be replaced. In replacing the original valve cage assembly rated at 1/2 tons, what would be the result if the replacement valve cage was oversized at 5 tons? GS-RA-07
A) The expansion valve would hunt excessively, alternately starving and overfeeding the evaporator coil.
B) The expansion valve would function normally, with the presentation of no problems.
C) The evaporator would be overfed producing consistently insufficient superheat.
D) The evaporator would be starved producing consistently excessive superheat.